[Date Prev][Date Next][Date Index]
Re: Software for fill-on-fill injection
- Subject: Re: Software for fill-on-fill injection
- From: Mohan Ramanathan <mohan@aps.anl.gov>
- Date: Mon, 28 Feb 2000 06:55:45 -0600 (CST)
Mark:
I have been seeing the trafic on this topic.
But let me clarify a few things on this topic.
> Folks,
>
> I am trying to modify my tomography software to work with fill-on-fill
> injection. What I need to do is the following:
>
> - ~60 seconds before a fill, stop data taking frames and take a final 'flat
> field' for normalization
>
> - After the fill wait ~60 seconds, take another flat field and then continue
> taking data frames
>
> In order to implement this I need PVs which provide the following information:
>
> - Next fill-on-fill injection will occur in N minutes
>
> - Previous fill-on-fill injection completed N minutes ago
>
> Obviously other PVs from which the above information can be derived would also
> be fine. Is such information currently available? I could not find it in the
> Web documentation. If it is not available am I the only one who thinks it is
> important to have?
>
> Mark Rivers
>
At this time all Fill-On-Fill is done manually. The announcement is made on the
PA system 10-15 minutes prior to commensement of fill-on-fill.
We can easily implement a few PV as per your requiremnts.
This can be done so that when the operator starts the procedure for fill-on-fill
we can start a fixed count down timer, which upon expiring will commense the
actual injection.
At the current time we have some PV which are used for top-up.
> My message related not to top-up mode, but to normal fill-on-fill operations.
> You are correct that the PVs listed above exist, however their values seem to
> be meaningless during normal operations. For example, right now:
> S:TopUpCurrent = 0.26746392
> S:TopUpTime = Feb 27, 2000 11:33:24
> S:TopUpInterval = 1.0000000
>
'S:TopUpCurrent' is the shot injection current. This is the last injection shot
fired and stored.
'S:TopUpTime' is the Time in Local time when the last injection shot was
performed. During fill-on-fill this will relate to the end of the injection.
'S:TopUpInterval' this process variable is derived from the secs since epoch
and is a whole number. So during top-up this will inform the time between
injection shots.
'S:TopUpIntervalAvg' is the average of 60 inejction shots. Under normal
injection conditions this will be 0.5 seconds as our injection frequency is 2
Hz.
In addition the following Process Variables are available for Top-Up:
Mt:TopUpTime2Inject.VAL Seconds remaining until injection (seconds).
Mt:TopUpWarning.VAL 10 second warning to injection.
More later.
mohan
-----------------------------------------------------------------
Mohan Ramanathan Beamline Operations
mohan@aps.anl.gov Advanced Photon Source
(630)-252-3773 Argonne National Laboratory